Skip to main content
Cart

Multiple embedment lengths in one design

Posted by Karl Biddleover 3 years ago
Multiple embedment lengths in one design

Hi, I would like to know if it is possible to use the HILTI anchor design with two threaded rods of different lengths.

threaded rod,embedment length

1 Reply
Posted by Samuel Aguiarover 3 years ago
Hilti Verified

Hi Karl,

Thanks for your question.

Post-installed anchors with different embedment lengths cannot be used in the same baseplate due to the potential differential deformation that can occur between the anchors. Differential deformation can result in additional stresses on the anchors and potentially lead to failure. The shorter anchors will tend to deform more than the longer ones, and as a result, they will likely carry more load and have higher stress levels. This uneven distribution of load can cause additional deformation, leading to the potential failure of the anchors.

However, please reach out to us via NZEngineers@hilti.com and we will be happy to check if we can give a recommendation for your specific case.

Kind Regards,
Samuel Aguiar