Posted by Venkat Gantiabout 3 years ago
HSU4-H Anchor screws,

i can see that the website shows 16mm screws where as the software only shows up to 14? Is there any other way or an equivalent that i can check my design for a 16mm?

HSU4-H,16MM

1 Reply
Posted by Samuel Aguiarabout 3 years ago
Hilti Verified

Hi Venkat,

Thanks for your question.

I believe you are trying to run a seismic design, right? The reason is because our HUS4-H 16 is not yet approved for seismic C2 category, and therefore Profis Engineering will not allow you to select this anchor, unless it is a static or Seismic C1 condition. One alternative would be using HST3 M16 if you want to use a mechanical 16 dia anchor for a Seismic C2 condition.

I will request one of our Field Engineers to contact you to provide support with your design.

Please do not hesitate to contact us should you have any other question.

Kind Regards,
Samuel Aguiar
Engineering Marketing Manager